bhalfweeg
Electrical
- Nov 8, 2002
- 8
I'm looking at possible designs for the distribution system of a new offshore installation with a maximum load of 70 MW supplied by 3 x LM6000 42 MW GTs. This immediately presents a problem of available switchgear fault and normal current ratings, with typical metalclad switchgear restricted to 11kV, 4000A, 50kA 3sec or 13.8 kV, 4000A, 40kA 3sec.
I've looked at the following fault level mitigation strategies:
1. fault limiting reactors
2. fault limiting fuses
3. step-up/step-down transformers
4. 22 kV generation and distribution
5. high-impedance generators
Since this is greenfield, I'm looking for more elegant solutions. Anyone come across such a scenario?
Cheers,
Brendan