We are doing a study on an existing plant and have found the symmetrical breaking capacities of some indoor metalclad Hawker Siddeley 11kV OCBs to be marginal (18,4kA). The prospective breaking fault current has been considered at 5 and 10 cycles (50Hz) (including motor contribution) giving respective maximum overloads of 13% at 5 cycles and 5% at 10 cycles.
Upgrading of the breakers would be an extremely costly excercise and the client does not have the money available. The other option is of course fault limiting reactors but this is also costly.
It would be interesting to hear some opinion on whether the potential 13%/5% breaking overload is acceptable, bearing in mind that the breakers, although well maintained are pretty old (20 years). Does anyone have any knowledge of the old manufacturing standards and what factors of safety were used when rating the OCBs?
Thanks and best regards
We are doing a study on an existing plant and have found the symmetrical breaking capacities of some indoor metalclad Hawker Siddeley 11kV OCBs to be marginal (18,4kA). The prospective breaking fault current has been considered at 5 and 10 cycles (50Hz) (including motor contribution) giving respective maximum overloads of 13% at 5 cycles and 5% at 10 cycles.
Upgrading of the breakers would be an extremely costly excercise and the client does not have the money available. The other option is of course fault limiting reactors but this is also costly.
It would be interesting to hear some opinion on whether the potential 13%/5% breaking overload is acceptable, bearing in mind that the breakers, although well maintained are pretty old (20 years). Does anyone have any knowledge of the old manufacturing standards and what factors of safety were used when rating the OCBs?
Thanks and best regards