engjg
Structural
- Jan 2, 2015
- 94
In design of a containment pit for an oil insulated transformer NFPA 850 5.5.2 states the "...should be sized to accommodate...(2)maximum expected number of fire hose operating for a maximum of 10 minutes"...an older version of NFPA 850 included this note (500 gpm operating for a minimum of 10 minutes) which as I understand it would give you 5000 gpm assuming you anticipate only one hose needed to fight fire for typical transformer....this provision seems to have been removed. I have another engineer citing the fire flow volume (which containment should accommodate) is based on 0.3 gal/sf/min for 10 minutes. I can not find the basis of this?