Today's challenge for the graybeards:
I must come up with a way to interface a new AC vector drive system (for a hoist) to an existing control cab for a GE DC M-G set drive system that was 50+ years old. The customer is insisting on retaining the existing operator control system that he says is using something called an "S21 regulator" on the Master Switch for speed control. It apparently takes a 120VAC source and splits it with a special transformer that has a moving coil with a variable air gap(?) so that if you push the handle forward from center, it drops the 120V as the air gap increases by 0-30VAC in-phase with the source, then if you pull the handle back past the center point, it drops the AC voltage by 0-30V, but at 180 degrees OUT of phase with the source. The phase difference becomes the sign of the signal, the 0-30V is the amplitude of the signal. This was then somehow fed into the M-G set power control to provide DC voltage control to the hoist motor.
I had, in my misspent youth, yanked out several Ward Leonard systems and replaced them with Solid State DC drives, but we NEVER retained any of the old operator interface systems so I never bothered to see what they were. I therefore have zero experience with this, but the guy I'm doing the project for insists these are (were) very common on old Ward Leonard and GE DC drive systems. Google is ignorant of the term "S21" with regard to anything speed control related, other than to confirm that is was indeed used on old crane controls. All I'm really looking for is a more accurate description of what it is/was and does so that I can come up with a way to transform it to something a modern drive can deal with, such as +-10VDC, but with a degree of accuracy one would expect for a hoist drive. A drawing would be fantastic.
I have by the way already offered to just replace the Master Switch with a more modern version, but he is insisting that anything that changes the operator's perception of how it works, real or not, is unacceptable. I MUST use the exiting system, although a transducer is acceptable once it leaves the control cab. Needless to say, I cannot find any sort of 0-30V In-Out of Phase to +-10VDC transducer and before I start cobbling together components to make one, I'd like a more accurate picture of what it is.
"Will work for (the memory of) salami"
I must come up with a way to interface a new AC vector drive system (for a hoist) to an existing control cab for a GE DC M-G set drive system that was 50+ years old. The customer is insisting on retaining the existing operator control system that he says is using something called an "S21 regulator" on the Master Switch for speed control. It apparently takes a 120VAC source and splits it with a special transformer that has a moving coil with a variable air gap(?) so that if you push the handle forward from center, it drops the 120V as the air gap increases by 0-30VAC in-phase with the source, then if you pull the handle back past the center point, it drops the AC voltage by 0-30V, but at 180 degrees OUT of phase with the source. The phase difference becomes the sign of the signal, the 0-30V is the amplitude of the signal. This was then somehow fed into the M-G set power control to provide DC voltage control to the hoist motor.
I had, in my misspent youth, yanked out several Ward Leonard systems and replaced them with Solid State DC drives, but we NEVER retained any of the old operator interface systems so I never bothered to see what they were. I therefore have zero experience with this, but the guy I'm doing the project for insists these are (were) very common on old Ward Leonard and GE DC drive systems. Google is ignorant of the term "S21" with regard to anything speed control related, other than to confirm that is was indeed used on old crane controls. All I'm really looking for is a more accurate description of what it is/was and does so that I can come up with a way to transform it to something a modern drive can deal with, such as +-10VDC, but with a degree of accuracy one would expect for a hoist drive. A drawing would be fantastic.
I have by the way already offered to just replace the Master Switch with a more modern version, but he is insisting that anything that changes the operator's perception of how it works, real or not, is unacceptable. I MUST use the exiting system, although a transducer is acceptable once it leaves the control cab. Needless to say, I cannot find any sort of 0-30V In-Out of Phase to +-10VDC transducer and before I start cobbling together components to make one, I'd like a more accurate picture of what it is.
"Will work for (the memory of) salami"