Old ABB DPU relay - 50 pickup set to 'F'

Status
Not open for further replies.

Uquresh1

Electrical
May 17, 2010
47
0
0
US
What does 'F' mean. I have a settings sheet for a DPU ABB relay. The 50P setting is shown to be 'F'. Does that mean it's OFF.
 
Replies continue below

Recommended for you

Take a look here:
Function 50 and 50P
thread238-268196
thread238-268196 said:
Before there were multifunction numerical relays, there would be a 50 relays for phase protection and a seperate 50 for zero sequence protection 50N. With the newer relays there needs to be a way of differentiating between the different available protective devises included within the one packaged relay. 50P, 50N, 50R, 67P, 67N..
thread238-268196 said:
The relay contains different functions, or modules, such as 50/51P for positive sequence, 50/51G for zero sequence (residual, ground), and 50/51Q for negative sequence currents.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 