switchnlight
Electrical
- Jan 4, 2005
- 7
Hallo forum members,
We have recently procured two 25MVA 66/33kV power transformers from a supplier in India. The transformers have an OLTC of single resistor type and they have put a caution that it is suitable for unidirectional power flow i.e. from HV to LV and not in the reverse. We however want to use this unit as a step up transformer supplying a radial feeder to a load at the 66kV end where power flow will always be in one direction. We therefore contacted the manufacturer to clarify this limitation in application of the tap changer. They informed us that it can only be used in the step down mode and not vice versa. They further said that the transformer could only be used as a step up unit with the tap changer utilized as an off load type or locked at one suitable tap position.
We consulted the J & P Transformer Book 1986 Ed. which says that “Tap changers constructed with one transition resistor are suitable for power flow in one direction only…… When two resistors are employed, the duty imposed on the diverter switch is unchanged by a change in the direction of power flow”. To our understanding the key words are "change in direction of power flow". This seems to imply that the restriction to unidirectional flow is when the transformer is used in bi-directional power flows such as when the transformer is connected in a ring or to generating sources on both HV and LV, which means that the flow of power may reverse. We see no reason why the magnitude and distribution of the circulating current in the diverter switch should be different for step-up and for step-down use of the tap changer. Can the experts in our forum kindly study our reasoning and advise if it is correct. Also kindly shed more light on this unidirectional and bidirectional designs for OLTCs.
We have recently procured two 25MVA 66/33kV power transformers from a supplier in India. The transformers have an OLTC of single resistor type and they have put a caution that it is suitable for unidirectional power flow i.e. from HV to LV and not in the reverse. We however want to use this unit as a step up transformer supplying a radial feeder to a load at the 66kV end where power flow will always be in one direction. We therefore contacted the manufacturer to clarify this limitation in application of the tap changer. They informed us that it can only be used in the step down mode and not vice versa. They further said that the transformer could only be used as a step up unit with the tap changer utilized as an off load type or locked at one suitable tap position.
We consulted the J & P Transformer Book 1986 Ed. which says that “Tap changers constructed with one transition resistor are suitable for power flow in one direction only…… When two resistors are employed, the duty imposed on the diverter switch is unchanged by a change in the direction of power flow”. To our understanding the key words are "change in direction of power flow". This seems to imply that the restriction to unidirectional flow is when the transformer is used in bi-directional power flows such as when the transformer is connected in a ring or to generating sources on both HV and LV, which means that the flow of power may reverse. We see no reason why the magnitude and distribution of the circulating current in the diverter switch should be different for step-up and for step-down use of the tap changer. Can the experts in our forum kindly study our reasoning and advise if it is correct. Also kindly shed more light on this unidirectional and bidirectional designs for OLTCs.