RalphChristie

Electrical
Jun 25, 2002
648
Dear all

Is there any difference between a master/slave configuration and a master/follower configuration for OLTC's (onload tap changers) on parallel transformers, or is it the same?

If there is a difference, what is it, and why do they use it?

Many thanks

RCC
 
Replies continue below

Recommended for you

Probably a method to remain politically correct.;-)

You think I'm kidding, but consider the following from a memo of the Los Angeles County Internal Services Department warning of offensive high-tech terminology:

"One such recent example included the manufacturer's labeling of equipment where the words 'Master/Slave' appeared to identify the primary and secondary sources. Based on the cultural diversity and sensitivity of Los Angeles County, this is not an acceptable identification label."

 
As jghrist says, the term "master/slave" is being replaced by "master/follower". No difference in functionality.

 
I've done some searching on google and found this site:

(see table 1)

master/follower - same transformers, same tap change
master/slave - same transformer, same tap change with permanent tap offset

but, why is there a permanent tap offset on the master/slave configuration?

Thanx




RCC
 
Suggestion: The permanent tap offset accounts for voltage drop between those two transformers, because of voltage drop along the feeder.
 
Small addition: The permanent offset also cover the voltage drop across the slave transformer.
 

RC—“Tap offset” may be to reduce circulating currents {er, var flow} between the paralleled transformers if they are not identical in electrical characteristics.
 

Also, "tap offset" could be used to force proportionate load sharing in differing size transformers.
 
Suggestion: Normally, the project engineering or conceptual phase covers power distribution voltage profile diagrams similar to IEEE Std 141-1993 (Red Book) Figure 3-4 Range A Voltage Profile Limits.
 