Simple question.
3-phase panel 4-wire 480/277.
I have a two wire resistive load 1000 watts@480VAC connected to L1-L2.
NO OTHER LOADS CONNECTED YET, nothing connected to neutral, nothing connected to L3
question
inside the wye connected transformer feeding the panel is one coil supplying 500KVA and one other coil supplying 500KVA?
 
Replies continue below

Recommended for you

Each coil, winding or phase is supplying 500 Watts.
Each coil is supplying 0.577 KVA.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Each coil in the transformer that supplied the load is taking 577.35 VA
 