Only the first coil of each winding group is blackened 1

Status
Not open for further replies.

EngRepair

Electrical
Oct 13, 2012
49
Only the first coil of each group is blackened.
What could be a reason?
Is it about corona discharge?
What is the remedy?
What to do during rewinding to avoid such an outcome?
The motor is TECO; 6,6 kV; 550 kW; six pole; DOL starting.
Thanks in advance.

106581912_1952475148222006_9034085011283538661_n_-_Copy_g4p7bo.jpg
 
Replies continue below

Recommended for you

ENG ,
this unusual occurrence was noticed in motor overhaul or you had problems with motor operation. If testing of insulation and Baker test do not see the problem, maybe the problem does not exist.
Good luck !
 
That is a head scratcher all right.
There are 18 equally spaced discolored areas, correct?
I claim that if this condition was related to normal operating voltage stress, then there would only be at most 9 locations. Let me explain my logic...

6-pole 18 groups. Groups are connected in alternating magnetic polarity:
A B' C A' B C' A B' C A' B C' A B' C A' B C'

If we label each group by an ordered pair of it's two terminations: (line neutral) for positive mag polarity and (neutral line) for negative mag polarity, then we have:
(Aline Aneutral)(Bneutral Bline)(Cline Cneutral)(Aneutral ALine)(Bline Bneutral)(Cneutral Cline)...

If we look at the 18 interfaces ")(" between coil groups: they are going to alternate between two patterns:
1 - one interface has two neutral end connections ...Aneutral)(Bneutral....
2 - the adjacent interface has two line end connections ....Bline)(Cline...
Only interface type 2 has a line end connection.
Do you agree? (maybe I am missing something).
If you guys agree, then we don't have the highest voltage stress at 18 equally-spaced locations around the circumference, we only have it at 9 equally spaced locations.
In that case it seems the pattern has nothing to do with normal operating voltage stress.

Even if I'm wrong on that, it certainly doesn't look like partial discharge. It's way to uniform accross the knuckle and down the slot for that.
You call it “blackening”. Is the red color the vpi resin color or something applied afterwards? To me it looks more like a surface red coating has disappeared to reveal the original vpi'd coil tape color below.


EDIT
Above I assume the 6 groups per phase are in parallel but that may be wrong.
If there are any series group connections then I'd think it is even fewer line end connections, although there are more possibilities for phase-to-phase combinations because there are also fewer neutrals.
It seems possible we have 18 group interfaces that have high voltage stress between adjacent coils at the end of each group.
If this scenario were applicable, the discoloration would have to be driven by partial phase to phase voltage differences between coils at the end of each group rather than phase to ground voltages at line end coils... still seems odd from the appearance although I see that each location involves two adjacent coils discoloring.
Can you describe how the groups are connected?


=====================================
(2B)+(2B)' ?
 
It's either contamination coating caused by static electric charge between the two phase coil groups, which can be wiped out by cleaning or it's partial discharge, which cannot be wiped out. Repair of PD depends on the amount of erosion of insulation.

Muthu
 
Yes, it looks like a corona discharge between the coil-groups.
This deterioration issue could be caused by insulation aging, poor epoxy impregnation, insufficient space between coils in endwinding, loose coils in slots, prolonged overheating, dirt or moisture pollutions, etc.
Necessary measurements should be performed in order to decide whether or not new rewind is needed.
Also, read the ABB white paper "Controlling partial discharge in high voltage motors and generators".

The basic winding diagram is attached ( one of several feasible).

[URL unfurl="true"]https://res.cloudinary.com/engineering-com/image/upload/v1594099143/tips/Trofazni_petljasti_namot_za_90_utora_i_6_pol_bqhqx6.pdf[/url]
 