Power pole has two hot lines(?2400v?) and neutral coming to it. These go to two transformers' primaries. The two Secondaries have one hot and one neutral wire coming out of each of them. The neutrals are tied together. The 3-phase voltages on the secondary are measured:
A-B, hot to neutral, 480v;
B-C, neutral to hot, 480v;
A-C, hot-to-hot, 480v!!!
This is an open delta. How can there be 480 across the two hots? What are the phase relationships? We are getting real wild voltage swings and spikes, even coming into a downstream, 3 phase transformer, with a 480 delta primary, and a 208/120 wye secondary. The control circuit comes off of one of the 120 line-to-neutral legs, and jumps around so much that relays and contactors are bouncing in and out by themselves. I'm ready to cal Scully and Mulder .
A-B, hot to neutral, 480v;
B-C, neutral to hot, 480v;
A-C, hot-to-hot, 480v!!!
This is an open delta. How can there be 480 across the two hots? What are the phase relationships? We are getting real wild voltage swings and spikes, even coming into a downstream, 3 phase transformer, with a 480 delta primary, and a 208/120 wye secondary. The control circuit comes off of one of the 120 line-to-neutral legs, and jumps around so much that relays and contactors are bouncing in and out by themselves. I'm ready to cal Scully and Mulder .