On an open delta three phase transformer in order to obtain a high leg voltage [208 V for instance] we take a full phase-let’s say a_b and a half of the other phase winding [a_n]
In my opinion, a half secondary winding transformer presents only 1/4 impedance [instead of 1/2 as it seems to be].
The short-circuit impedance of a transformer viewed from secondary side it is as follows:
Zab=Z'pab+Zsab
where Z'pab = secondary referred primary impedance Zpab*ksp
ksp=(no.turns.sec[ws]/no.turns.primary[wp])^2
Zsab=Rsab+Xsab.i complex secondary impedance.
Xsab=kxs*ws^2
where kxs it is a constant which depends on frequency and magnetic circuit geometry.
If we split the secondary winding wsnew=ws/2 then Xan=Xsab/4 and kspan=(ws/2/wp)^2=kspab/4
Only Rsan=Rsab/2 but it will be negligible so Zan≈Zab/4=ZT/4.