- Oct 1, 2002
- 1
I have two transformers connected in an open delta configuration providing 120/240V loads. The two transformers are 50kVa and 25kVA with the 50kVA center tapped. I recently experienced some significant damage to my 3 phase panel. Turns out that the neutral and one of the phase conductors shorted and open circuited at the utility pole. The resultant fault also opened the 50kVA cutout (12A). The 25kVA transformer and cutout (3A) were unaffected, possibly continuing to provide power to the building via the "wild leg" conductor. My question is this, the 3 phase panel took a serious beating, lots of arcing damage, is it possible that the panel backplane was exposed to utility line voltage (7200V to ground in this case)?