fpst
Computer
- Jan 20, 2012
- 109
The annex of NFPA 13 2007 defines Open-Grid Ceilings in A.3.7.2 (2): "The term open-grid ceilings as used in this standard refers to ceilings in which the openings are 1 ⁄ 4 in. (6.4 mm) or larger in the least dimension, the thickness of the ceiling material does not exceed the least dimension of the openings, and the openings constitute at least 70 percent of the ceiling area."
My question is what if you have a room which has 70% or more of it's ceiling area constituted of return and supply duct opening space (such as a small room with an unusually high number of supply/return ducts)? Obviously, heat could escape through these openings and delay sprinkler operation, but what about the 1/4" wording above? I'm having trouble deciphering its meaning.
My question is what if you have a room which has 70% or more of it's ceiling area constituted of return and supply duct opening space (such as a small room with an unusually high number of supply/return ducts)? Obviously, heat could escape through these openings and delay sprinkler operation, but what about the 1/4" wording above? I'm having trouble deciphering its meaning.