HamburgerHelper
Electrical
- Aug 20, 2014
- 1,127
Our system has an issue with detecting an open phase or an open phase with a jumper that swings down into the phase below it in our distribution system. The arrangement is a step down delta-wye grounded transformer in the substation that feeds a bunch of wye-ground-wye-ground distribution transformers in the field. There is a programmable relay in the substation, the distribution transformers are fused, and there is a mix mash of automated and comm. controlled reclosers in the field.
When I first was told this problem, my first response was to use negative sequence or a I2/I1 ratio to detect an open phase. The problem I am seeing with this is that if your jumper fails near the end of the feeder, you will have a hard time detecting an open phase with I2 or an I2/I1 ratio without making them overly sensitive. All the other transformers further up the feeder drawing I1 will make it difficult to see the open phase from the substation. Someone brought up to have the relay alarm on large step changes of negative sequence current. I don't know how well that works. Nor do I like the idea of having to investigate each arrangement to determine what a "large" step change is.
How do you guys go about tackling this problem?
When I first was told this problem, my first response was to use negative sequence or a I2/I1 ratio to detect an open phase. The problem I am seeing with this is that if your jumper fails near the end of the feeder, you will have a hard time detecting an open phase with I2 or an I2/I1 ratio without making them overly sensitive. All the other transformers further up the feeder drawing I1 will make it difficult to see the open phase from the substation. Someone brought up to have the relay alarm on large step changes of negative sequence current. I don't know how well that works. Nor do I like the idea of having to investigate each arrangement to determine what a "large" step change is.
How do you guys go about tackling this problem?