jghrist
Electrical
- Jul 16, 2002
- 4,219
One of our municipal clients had a situation where someone shot one phase on their wholesale power supplier's 100 kV transmission line serving the client's 100-25 kV substation. The phase opened but no trip occurred, leaving a phase open on the primary of the delta-wye transformer. In this situation, two of the secondary phases are 50% of nominal phase-to-neutral and 180 degrees out of phase from the third phase.
This caused considerable damage to our client's customers' motors.
This situation can be detected using some undervoltage logic on the 25 kV side. It can also be distinguished from a VT fuse blowing situation. This protection was not provided, however.
Have any utility people out there had similar occurrances? Do you normally (ever?) provide protection against this at distribution substations? If so, do you trip the station or just send a SCADA alarm?
This caused considerable damage to our client's customers' motors.
This situation can be detected using some undervoltage logic on the 25 kV side. It can also be distinguished from a VT fuse blowing situation. This protection was not provided, however.
Have any utility people out there had similar occurrances? Do you normally (ever?) provide protection against this at distribution substations? If so, do you trip the station or just send a SCADA alarm?