Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Open Web Steel Joist - Depth reduction

Status
Not open for further replies.

CROWN06

Structural
Apr 19, 2006
32
I have existing 24 inch deep steel joist spanning 40 feet. At one end, for about twelve feet I need to reduce the depth to 12 inches. Any ideas.
 
Replies continue below

Recommended for you

The optimum depth for your joists should be about 28 to 30"... ' your 24" is a little shallow... and might be prone to some vibration. Cutting it to 12" for 1/3 the span will likely cause problems... you might try something else...

Dik
 
Intermediate support of the joist via column, wall, beam - at the point where the joist must be reduced. Re-analyze the joists's shear moment diagram capacity and verify that intermediate web strengthening is OK or needs strengthening.

 
Suppose at cut we drop a column. For 12 feet we can add a steel beam and remove the joist. For the remaining joist still in service with new support at column, do we need to do any modifications or simply add vertical member (web stiffener) at column top should be fine
 
I am in agreement with JAE's recommendation.

The shortened joist's web members need to be looked at in that some of those web members may have stress reversals from the original design.
 
Yep - Crown06 - just to repeat - when you design a joist, it has a theoretical shear capacity that varies across the span from the original max. end reaction - to 0 at midspan. However, the SJI requires the joist manufacturers to at least design the joist web members for 25% of the shear at the end (some years ago it was 50% so the older the joist the more hefty the webs).

When you shorten a joist span, you have the potential to create a larger shear at the new end from what it was originally designed for. Simply construct an "original" shear diagram and superimpose it over your new shear diagram to check if you are ok.

 
Status
Not open for further replies.

Part and Inventory Search

Sponsor