Fellas,
I have a project that I have been working on for about two weeks that I could use some advise/suggestions on.
We have an area of our distribution system that is above our normal HGL. The system was built by a developer in the 60's and we "inherited" it shortly after. The current system has two small pumps that feed a 70,000 gallon tank which in turn provides water to about 25 homes and 4 fire hydrants. Due to the high elevation difference between the tank and hydrants, they can currently flow 1,000+ GPM.
We want to remove the existing set-up and replace it with a constant pressure VFD pumping system (due to poor water quality from lack of turnover in the system). The new pump station will be able to provide approximately 600 GPM.
My problem comes into play when the fire hydrants are opened. The available head can produce a flow of 1,000+ GPM while the pump station can only produce 600 GPM. We can not justify a larger pump station for 25 homes so I am wanting to throttle the flow at the hydrants.
To reduce the flow, I looked at PRVs/Pressure Sustaining Valves first. However these valves are expensive, will require maintenance, and we will need multiple ones due to loops in the system.
The second option is to install an orifice plate in the hydrant legs to control the amount of flow that the hydrant can produce. This flow would be limited to a little over 500 gpm @ 20 psi (Local Regulation minimum).
Have ya'll used anything like this or seen a similar set-up/scenario before? Do you know of a good orifice plate manufacturer?
Any advice is greatly appreciated.
Thanks
Tyler
I have a project that I have been working on for about two weeks that I could use some advise/suggestions on.
We have an area of our distribution system that is above our normal HGL. The system was built by a developer in the 60's and we "inherited" it shortly after. The current system has two small pumps that feed a 70,000 gallon tank which in turn provides water to about 25 homes and 4 fire hydrants. Due to the high elevation difference between the tank and hydrants, they can currently flow 1,000+ GPM.
We want to remove the existing set-up and replace it with a constant pressure VFD pumping system (due to poor water quality from lack of turnover in the system). The new pump station will be able to provide approximately 600 GPM.
My problem comes into play when the fire hydrants are opened. The available head can produce a flow of 1,000+ GPM while the pump station can only produce 600 GPM. We can not justify a larger pump station for 25 homes so I am wanting to throttle the flow at the hydrants.
To reduce the flow, I looked at PRVs/Pressure Sustaining Valves first. However these valves are expensive, will require maintenance, and we will need multiple ones due to loops in the system.
The second option is to install an orifice plate in the hydrant legs to control the amount of flow that the hydrant can produce. This flow would be limited to a little over 500 gpm @ 20 psi (Local Regulation minimum).
Have ya'll used anything like this or seen a similar set-up/scenario before? Do you know of a good orifice plate manufacturer?
Any advice is greatly appreciated.