BravoCompany
Mechanical
- Mar 19, 2004
- 27
Typically I've seen the HVAC industry's most common rule of thumb for sizing low velocity duct to be:
(.08-.1 " wc/100 ft) for supply duct.
(.05" " wc/100 ft) for return duct.
Does anyone know if these values are published and if so where exactly?
Why the discrepancy between values?
I was taught to use these values some time ago and have since heard several different lines of reasoning.
My assumption has always been that the lower value on return side offers more equal pressure equalization between spaces-- no doors slamming shut etc. The realized advantage being that no balance dampers are required on the return air side of the system. This assumption is only speculation.
Looking at the 2005-ASHRAE Fundamentals Chapter 35 Fig 9 along with the explanation under Equal Friction Sizing Method. One questions the .05 " wc/100 ft.
I would be interested to hear what anyone else may know or wish to discuss regarding these values.
Would anyone like to comment?
(.08-.1 " wc/100 ft) for supply duct.
(.05" " wc/100 ft) for return duct.
Does anyone know if these values are published and if so where exactly?
Why the discrepancy between values?
I was taught to use these values some time ago and have since heard several different lines of reasoning.
My assumption has always been that the lower value on return side offers more equal pressure equalization between spaces-- no doors slamming shut etc. The realized advantage being that no balance dampers are required on the return air side of the system. This assumption is only speculation.
Looking at the 2005-ASHRAE Fundamentals Chapter 35 Fig 9 along with the explanation under Equal Friction Sizing Method. One questions the .05 " wc/100 ft.
I would be interested to hear what anyone else may know or wish to discuss regarding these values.
Would anyone like to comment?