Suggestion: The automatic synchronization prevents the breaker closure, when the voltage difference between the breaker open contact terminals is excessive, e.g. more than 10V. However, the automatic synchronizer has to have specified:
1. Upper voltage limit for both potential inputs, which is variable from a minimum, e.g. 110V to 140V AC accurate to within e.g. ±2% of full scale.
2. Lower voltage limit for both potential inputs, which is variable from a minimum, e.g. 90V to 120V AC accurate to within e.g. ±2% of full scale.
3. Differential frequency limit, which is variable from a minimum of e.g. 59.5Hz to 60.5Hz and accurate to within e.g. ±5% of full scale.
These are necessary requirements to establish the safe synchronization.
E.g., if there is a "180deg out of phase" one phase across one open circuit breaker contact, the differential voltage may be satisfied, e.g. equal to zero, however, if the upper voltage limit is not 110V and lower voltage limit is not 90V, then the circuit breaker will not close.