DRSCHON
Electrical
- Apr 13, 2016
- 1
Outdoor Less Flammable Liquid package substation with Fire rated wall enclosure and open roof does required any kind of fire protection,
450.27 Oil-Insulated Transformers Installed Outdoors.
Combustible material, combustible buildings, and parts of
buildings, fire escapes, and door and window openings shall
be safeguarded from fires originating in oil-insulated transformers
installed on roofs, attached to or adjacent to a building
or combustible material.
In cases where the transformer installation presents a fire
hazard, one or more of the following safeguards shall be applied
according to the degree of hazard involved:
(1) Space separations
(2)Fire-resistant barriers
(3)Automatic fire suppression systems
(4) Enclosures that confine the oil of a ruptured transformer
tank
We have a fire rated cmu wall enclose and can we say that its a Fire Resistant barriers and We are not using Automatic Fire suppression System or any thing
450.27 Oil-Insulated Transformers Installed Outdoors.
Combustible material, combustible buildings, and parts of
buildings, fire escapes, and door and window openings shall
be safeguarded from fires originating in oil-insulated transformers
installed on roofs, attached to or adjacent to a building
or combustible material.
In cases where the transformer installation presents a fire
hazard, one or more of the following safeguards shall be applied
according to the degree of hazard involved:
(1) Space separations
(2)
(3)
(4) Enclosures that confine the oil of a ruptured transformer
tank
We have a fire rated cmu wall enclose and can we say that its a Fire Resistant barriers and We are not using Automatic Fire suppression System or any thing