Three ABB ACS850 drives installed in our facility for different applications started to trip with over current(different occasions). After ruling out the possibilities of over current due to load issues, defective motor and cables, we found that value of measuring parameter 01.07(DC-voltage) is < 350V which is far less than expected value 680 volts. Please note that drives are connected with 3 phase 480 v A/C Supply. Actual DC-Voltages, we measured on DC bus with our Fluke device were 680 Volts. Drives were replaced with new units and problem was resolved.
I request you to give expert opinion regarding the problem.
I request you to give expert opinion regarding the problem.