Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

Overcurrent in DCS/PLC SCADA

Status
Not open for further replies.

Histor

Electrical
Mar 2, 2022
70
0
0
SG
Hi,
How can I monitor the over current value of the motor in PLC SCADA?
The motor is running with DOL starter.
 
Replies continue below

Recommended for you

Most control manufacturers now offer “smart” overload relays that have communication options either built in or optional. The chances are good that if you contact the manufacturer of your DOL starters, they have a smart OL that will replace the OL relay that you have now and correct directly to the contactor.


" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
 
Status
Not open for further replies.
Back
Top