a10jp
Electrical
- May 18, 2005
- 150
At one of the job site we have, the service transformer at the utility pole is 3x 75KVA which gives 225kVA max capacity. Our contractor has previously procured a 1200A main service panel with a 1200A main circuit breaker, before he realized what the utility service will be. At 225KVA, the max secondary current would be 625A or OCP would be 800A service.
Therefore 1200A is not effectively protecting the secondary, which according to NEC 2008, Art 450, cannot be more than 125% if secondary overcurrent protection is used based on NEC.
I am looking at the rationale whether we need to change out the 1200A service, and at the same time, looking at the angle that with 1200A secondary you are effectively eliminating the secondary protection, which results in only primary protection on the transformer fuse cutouts, which under certain condition maybe allowed by Code (Primary protection only).
Because it is my understanding that the utility can decide to put their equipment based on the burn rate of consumption, perhaps this is common, but in this case I want to be certain our installation is code compliant and safe. What are your opinions? Thanks for your help!
Therefore 1200A is not effectively protecting the secondary, which according to NEC 2008, Art 450, cannot be more than 125% if secondary overcurrent protection is used based on NEC.
I am looking at the rationale whether we need to change out the 1200A service, and at the same time, looking at the angle that with 1200A secondary you are effectively eliminating the secondary protection, which results in only primary protection on the transformer fuse cutouts, which under certain condition maybe allowed by Code (Primary protection only).
Because it is my understanding that the utility can decide to put their equipment based on the burn rate of consumption, perhaps this is common, but in this case I want to be certain our installation is code compliant and safe. What are your opinions? Thanks for your help!