- Sep 14, 2001
- 44
Hi,
I have a customer who has asked that a 13.8kV feed be fed overhead about a mile to a 13.8kv/4.16kV transformer. NESC says that a ground connection should be made to the neutral at the source. The issue is the switchgear that will be feeding this line is only 3W 3PH. Where do I get my ground? It would seem that I would want one to run with the phases. Do you think just connecting to the ground grid at the source and then grounding every couple of poles would be the correct way to look at this? And if so would I run the ground below the phases as a neutral would be typically run or would this become in essence a shield wire and need to be located above the phases?
Thanks,
Doug
I have a customer who has asked that a 13.8kV feed be fed overhead about a mile to a 13.8kv/4.16kV transformer. NESC says that a ground connection should be made to the neutral at the source. The issue is the switchgear that will be feeding this line is only 3W 3PH. Where do I get my ground? It would seem that I would want one to run with the phases. Do you think just connecting to the ground grid at the source and then grounding every couple of poles would be the correct way to look at this? And if so would I run the ground below the phases as a neutral would be typically run or would this become in essence a shield wire and need to be located above the phases?