After moving to Canada 6 years ago, I have been walking for a small utility that predominantly works with generation and transmission but also dabbles in small amounts of distribution. One significant difference between Canada and my native country is that the medium-voltage distribution system typically includes a neutral conductor, which is generally connected to source and destination substation earth grids as well as being connected to earth every so many poles outside of the substation.
From what I gather, this neutral conductor has quite a number of uses:
1/ Canadian (and US) practice is to use a large number of small step-down single-phase transformers connected phase-neutral, as compared with using larger three-phase transformers connected in delta, or, where single phase power is needed, single-phase transformers connected phase-to-phase. This practice requires a neutral conductor.
2/ The neutral conductor is often used by line crews as an earthing point while establishing their earthing and equipotential zones when working on lines and equipment.
3/ The interconnection of the earth grids for all substations (via the neutral conductor running between each substation) combined with the earthing at many poles creates a much lower impedance to the general mass of earth, reducing GPR in substations.
4/ In the event of a downed conductor, there is some chance that the conductor may contact the neutral resulting in a readily detectable fault current (especially in areas prone to high impedance faults).
From my own observations and "discussions" with various colleagues, I have a several questions:
A/ Apparently in some areas in Canada, the practice is not to connect the neutral conductor into the substation earth grid, to ensure that GPR is not transferred from the substation out onto the distribution system (especially bearing in mind that pole ground locations etc won't use crushed rock etc to limit step and touch potentials). While I can appreciate the desire, surely this results in the general mass of earth being used as the return path for the various phase-to-ground connected transformers on the distribution system?
B/ How is the issue of GPR being transferred to the distribution system handled? Is it simply assumed that the GPR will be low enough, and the impedance of the neutral conductor relative to the many pole-grounds such that the GPR is not going to be a concern? Do utilities sometimes include switch in the connection from neutral conductor to substation earth to allow this to be isolated while line crews are undertaking work?
C/ How significant is the improvement in detection of downed conductors? It seems to me that, unless the conductor contacts the neutral conductor or lands very close to a pole ground, most faults would be similar regardless of the presence of a neutral conductor.
D/ In addition to a 25 kV distribution system, we also have a 35 kV system that is effectively a subtransmission system about town. It has no phase-to-ground connected loads, with all loads being three-phase transformers with delta HV connections. This negates the first reason above to have the neutral conductor, but I note that a neutral conductor is still present for each line. I assume that this is for the other three reasons listed, but are these really sufficient to justify the additional cost? I ask this because we occasionally run short sections of line to connect our generation into their system, and could probably quite easily get away with omitting the neutral conductor.
Any comments on the above would be appreciated.
Thanks,
mgtrp
After moving to Canada 6 years ago, I have been walking for a small utility that predominantly works with generation and transmission but also dabbles in small amounts of distribution. One significant difference between Canada and my native country is that the medium-voltage distribution system typically includes a neutral conductor, which is generally connected to source and destination substation earth grids as well as being connected to earth every so many poles outside of the substation.
From what I gather, this neutral conductor has quite a number of uses:
1/ Canadian (and US) practice is to use a large number of small step-down single-phase transformers connected phase-neutral, as compared with using larger three-phase transformers connected in delta, or, where single phase power is needed, single-phase transformers connected phase-to-phase. This practice requires a neutral conductor.
2/ The neutral conductor is often used by line crews as an earthing point while establishing their earthing and equipotential zones when working on lines and equipment.
3/ The interconnection of the earth grids for all substations (via the neutral conductor running between each substation) combined with the earthing at many poles creates a much lower impedance to the general mass of earth, reducing GPR in substations.
4/ In the event of a downed conductor, there is some chance that the conductor may contact the neutral resulting in a readily detectable fault current (especially in areas prone to high impedance faults).
From my own observations and "discussions" with various colleagues, I have a several questions:
A/ Apparently in some areas in Canada, the practice is not to connect the neutral conductor into the substation earth grid, to ensure that GPR is not transferred from the substation out onto the distribution system (especially bearing in mind that pole ground locations etc won't use crushed rock etc to limit step and touch potentials). While I can appreciate the desire, surely this results in the general mass of earth being used as the return path for the various phase-to-ground connected transformers on the distribution system?
B/ How is the issue of GPR being transferred to the distribution system handled? Is it simply assumed that the GPR will be low enough, and the impedance of the neutral conductor relative to the many pole-grounds such that the GPR is not going to be a concern? Do utilities sometimes include switch in the connection from neutral conductor to substation earth to allow this to be isolated while line crews are undertaking work?
C/ How significant is the improvement in detection of downed conductors? It seems to me that, unless the conductor contacts the neutral conductor or lands very close to a pole ground, most faults would be similar regardless of the presence of a neutral conductor.
D/ In addition to a 25 kV distribution system, we also have a 35 kV system that is effectively a subtransmission system about town. It has no phase-to-ground connected loads, with all loads being three-phase transformers with delta HV connections. This negates the first reason above to have the neutral conductor, but I note that a neutral conductor is still present for each line. I assume that this is for the other three reasons listed, but are these really sufficient to justify the additional cost? I ask this because we occasionally run short sections of line to connect our generation into their system, and could probably quite easily get away with omitting the neutral conductor.
Any comments on the above would be appreciated.