Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Overhead line operation

Status
Not open for further replies.

Adam1980

Electrical
Feb 17, 2012
87
Dear all,

is there any negative impact of operating one circuit of a double circuit overhead line at a lower voltage than its rating.
For example having double circuit 225 kV line and operating one circuit at 225 kV and the other at 33 kV.

From my perspective since it is a lower voltage there will be no problem with insulation or clearing distance. Of course the power transfer will be limited due to the higher current. Another issue could be overvoltage protection equipment at the transfer from 33 kV to 225 kV since if they are not sized properly they might not function as required!

Any other concerns that one should care for!

Thanks!
 
Replies continue below

Recommended for you

If the lines are of any length, then voltage drop may limit the capacity before over current does.
Why do you want to do this?

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Actually it's not that uncommon to have a line built for one voltage and operated at a lower voltage, though perhaps not at a nearly 7:1 ratio. We have a number of places where line constructed as 230kV are used for 115kV circuits and lines built for 115kV operated at 57kV. The insulation system is obviously over rated, but any arrestors need to be appropriate for the operating voltage, not the constructed voltage.
 
Status