bklauba
Industrial
- Sep 22, 2003
- 285
As requested, this is a new thread, taking up the subject of: For purposes of both safety and ease of diagnosis, where is the best place to put NC contacts that deny activation of a motor contactors: 'Tween the contacts and neutral or 'tween contacts and hot feed to coil?
Below is the exchange that led to this issue, and my apologies for changing the subject on "fused neutral" thread.
jistre (Mechanical) 26 Mar 08 14:02
Heck, I only took Volts for Dolts in college, and I know enough to say "YIKES!" on this one. The first maintenance guy who assumes that the equipment is de-energized because the breaker's open is going to be very shocked to find out he's wrong.
bklauba (Industrial) 26 Mar 08 14:32
. . . . which is why putting a NC Overload contact 'tween a contactor coil and neutral sure looks like tortured logic. (Sorry if you guys think this is a subject change, but, not really.) Putting it "in front" of the coil, so the coil gets NO JUICE when the NC Overload contact is open seems just so right!
BK
Below is the exchange that led to this issue, and my apologies for changing the subject on "fused neutral" thread.
jistre (Mechanical) 26 Mar 08 14:02
Heck, I only took Volts for Dolts in college, and I know enough to say "YIKES!" on this one. The first maintenance guy who assumes that the equipment is de-energized because the breaker's open is going to be very shocked to find out he's wrong.
bklauba (Industrial) 26 Mar 08 14:32
. . . . which is why putting a NC Overload contact 'tween a contactor coil and neutral sure looks like tortured logic. (Sorry if you guys think this is a subject change, but, not really.) Putting it "in front" of the coil, so the coil gets NO JUICE when the NC Overload contact is open seems just so right!
BK