Hi all,
I have one VFD controlling 2 motors (motor are connected to cascaded pumps which operates on the same speed and on the same pipeline).
The motor is rated 2,500 HP, 4,000 V, 3 phase, 43 Hertz, 12 pole, SF = 1.0, making it rated for 430 RPM synchronous speed. The VFD output voltage is 4,160 V. The actual pump speed requirement is 350 RPM and process operators may tend to vary the pump speed depending on the process "through-put" requirements which varies on the liquid density on the pipes. The VFD output section have isolation switch for each motor feeder, with phase CTs connected to GE 339 relays. Each motor RTDs are wired to each GE 339 relay.
I do understand that when inverter duty motors are driven below synchronous speed, the volts/Hz at the motor must be maintained to keep torque capacity. This, theoretically, would require a reduction of VFD output voltage, which in turn can increase the running motor current (if the same work is maintained at the motor) However, the pump actual mechanical torque imposed on the motor should be less than 2,500 HP, that the current may still be less than the motor FLA.
Therefore, whether the motor (or VFD or the motor power cable) will get overloaded (current-wise) or not, will all depend on the amount of work (Pump Torque) imposed to it at a particular speed level. This makes the VFD and process operators given the capability to operate at any varying speed and "process output" requirements. Since the VFD will be set to the standard motor nameplate voltage and frequency...that is V/Hz setting will be 4,000/43 = 93.023, this will be kept by the VFD in relation to its internal protection and control.
So now, if the VFD's individual GE 339s protection settings were to be set, this is how I perceive it philosophically:
1. Individual GE 339 overload setting will still going to be set NOT TO EXCEED 115% motor rated FLA, regardless of VFD operation
2. Individual GE 339 overload setting will still be set to the left of the motor hot and cold damage curves, regardless of VFD operation
3. On the protection and coordination Time-Current-Curves (TCCs), the current overload curve will be set, AS IF THE MOTOR WAS STARTED DIRECT-ON-LINE
4. The motor FLA is still as per nameplate regardless how the VFD will operate and should not be exceeded to maintain rated motor life expectancy
For the VFD, it only sees the summation of motor load currents by the two motors running. Hence, the manufacturer will set the VFD based on the motors' rated V/Hz and its internal protection will be set to protect itself based on this current summation. The VFD has an inherent overload capacity at 150% for minutes of operation only and will shutdown after such time has elapsed. If the sum of the motor current drawn at 350 RPM (35 Hz), depending on pump loading, hits the VFD's internal overload region, then the motors will be stopped at a certain time delay.
If the motor manufacturer would confirm that their motor design can operate at a percentage, a bit beyond motor nameplate FLA, then motors may be driven (by process operators) at a point where the their summation hits the VFD overload region. In such case, the VFD overload capability may have to be reduced from 150% setting to a less than 150% (say 125% and the 25% taken out will be added as continuous capability). At the end of the day, the VFD have a maximum current capacity rating at 0% overload capability. On an extreme case, the VFD overload capacity will be set to 0% and the VFD can output its maximum current rating (which is significantly larger than the sum of motor nameplate FLA), allowing the process operators to more flexibility on the VFD control....and the motors' GE 339s current O/L will be set to protect the motor individually so as not to hit their damage curves.
I will appreciate any comments from experienced VFD folks here in terms on my statements on the GE 339 overload settings and the last couple of paragraphs. Of course, I will be coordinating with both VFD and motor manufacturer.
Thank you in advance.
I have one VFD controlling 2 motors (motor are connected to cascaded pumps which operates on the same speed and on the same pipeline).
The motor is rated 2,500 HP, 4,000 V, 3 phase, 43 Hertz, 12 pole, SF = 1.0, making it rated for 430 RPM synchronous speed. The VFD output voltage is 4,160 V. The actual pump speed requirement is 350 RPM and process operators may tend to vary the pump speed depending on the process "through-put" requirements which varies on the liquid density on the pipes. The VFD output section have isolation switch for each motor feeder, with phase CTs connected to GE 339 relays. Each motor RTDs are wired to each GE 339 relay.
I do understand that when inverter duty motors are driven below synchronous speed, the volts/Hz at the motor must be maintained to keep torque capacity. This, theoretically, would require a reduction of VFD output voltage, which in turn can increase the running motor current (if the same work is maintained at the motor) However, the pump actual mechanical torque imposed on the motor should be less than 2,500 HP, that the current may still be less than the motor FLA.
Therefore, whether the motor (or VFD or the motor power cable) will get overloaded (current-wise) or not, will all depend on the amount of work (Pump Torque) imposed to it at a particular speed level. This makes the VFD and process operators given the capability to operate at any varying speed and "process output" requirements. Since the VFD will be set to the standard motor nameplate voltage and frequency...that is V/Hz setting will be 4,000/43 = 93.023, this will be kept by the VFD in relation to its internal protection and control.
So now, if the VFD's individual GE 339s protection settings were to be set, this is how I perceive it philosophically:
1. Individual GE 339 overload setting will still going to be set NOT TO EXCEED 115% motor rated FLA, regardless of VFD operation
2. Individual GE 339 overload setting will still be set to the left of the motor hot and cold damage curves, regardless of VFD operation
3. On the protection and coordination Time-Current-Curves (TCCs), the current overload curve will be set, AS IF THE MOTOR WAS STARTED DIRECT-ON-LINE
4. The motor FLA is still as per nameplate regardless how the VFD will operate and should not be exceeded to maintain rated motor life expectancy
For the VFD, it only sees the summation of motor load currents by the two motors running. Hence, the manufacturer will set the VFD based on the motors' rated V/Hz and its internal protection will be set to protect itself based on this current summation. The VFD has an inherent overload capacity at 150% for minutes of operation only and will shutdown after such time has elapsed. If the sum of the motor current drawn at 350 RPM (35 Hz), depending on pump loading, hits the VFD's internal overload region, then the motors will be stopped at a certain time delay.
If the motor manufacturer would confirm that their motor design can operate at a percentage, a bit beyond motor nameplate FLA, then motors may be driven (by process operators) at a point where the their summation hits the VFD overload region. In such case, the VFD overload capability may have to be reduced from 150% setting to a less than 150% (say 125% and the 25% taken out will be added as continuous capability). At the end of the day, the VFD have a maximum current capacity rating at 0% overload capability. On an extreme case, the VFD overload capacity will be set to 0% and the VFD can output its maximum current rating (which is significantly larger than the sum of motor nameplate FLA), allowing the process operators to more flexibility on the VFD control....and the motors' GE 339s current O/L will be set to protect the motor individually so as not to hit their damage curves.
I will appreciate any comments from experienced VFD folks here in terms on my statements on the GE 339 overload settings and the last couple of paragraphs. Of course, I will be coordinating with both VFD and motor manufacturer.
Thank you in advance.