I have problem with motor pump in my factory.
I utilized Teco motor 11kW 2 pole 3 phase. this motor overloaded for unknown reason.
this motor is currently replaced because the previous has unstable electrical current. after the replacement, electrical current was good until yesterday, the motor started to overloaded and shut off automatically. and i have no idea what's going on.
FYI, when I try to maximize water flow, electric current is going up to 24.7A and when minimized it's decrease to 22.7A. is it normal?
Another engineer said that it was because of the impeller. but I think it's because of the motor or something related to the motor.
does anyone know how to fix this problem since I am lack of water for production?
Thanks in advance for your help. big appreciation for you..