MEP.Learner
Mechanical
- Jul 22, 2016
- 26
hi Engineers,
I have a project in tropical country, and issue that aircon probably oversized and have humidity issue (more than 70% RH obtained), with mold growing on walls observed.
This may also due to hot humid air infiltration to the A/C space.
Would like to ask for advice and opinion how this can be solved.
From Trane aircon design notes that, when sensible heat ratio is lower due to certain reason (like space is at partial heat load), it will end up higher to obtain higher RH% which result in the mold issue.
See <attached> for illustration from the notes.
I am wondering, if any aircon setting can be adjusted to improve this situation.
As my system is a Chilled water system, with a adjustable fan speed FCU.
Would it help by adjusting the setting hoping to achieve lower SHR (sensible heat ratio) by getting lower off coil temperature and lower airflow air (so not too much over cooling).. so to meeting the space's SHR thus getting the moisture controlled.
Or is there is any moisture absorbing material that can be added to the system?
Appreciate if there is any valuable input. Thanks.
I have a project in tropical country, and issue that aircon probably oversized and have humidity issue (more than 70% RH obtained), with mold growing on walls observed.
This may also due to hot humid air infiltration to the A/C space.
Would like to ask for advice and opinion how this can be solved.
From Trane aircon design notes that, when sensible heat ratio is lower due to certain reason (like space is at partial heat load), it will end up higher to obtain higher RH% which result in the mold issue.
See <attached> for illustration from the notes.
I am wondering, if any aircon setting can be adjusted to improve this situation.
As my system is a Chilled water system, with a adjustable fan speed FCU.
Would it help by adjusting the setting hoping to achieve lower SHR (sensible heat ratio) by getting lower off coil temperature and lower airflow air (so not too much over cooling).. so to meeting the space's SHR thus getting the moisture controlled.
Or is there is any moisture absorbing material that can be added to the system?
Appreciate if there is any valuable input. Thanks.