When checking the overturn factor of safety provided in Enercalc vs. the method used in “Foundation and Anchor Design Guide for Metal Building Systems” by Alexander Newman, I found some discrepancies. Rotation is considered around point A.
Enercalc, Case 1:
Resisting Moment, Mres = L/2*(F2+w1+w2)
Applied OT Moment, Mot = F1*H
Enercalc, Case 2:
Resisting Moment, Mres = L/2*(w1+w2)
Applied OT Moment, Mot = (F1*H)+(F2*L/2)
-------------------------------------------------------------
Text Ref., Case 1: (Same as Enercalc)
Resisting Moment, Mres = L/2*(F2+w1+w2)
Applied OT Moment, Mot = F1*H
Text Ref., Case 2:
Resisting Moment, Mres = L/2*(w1+w2-F2)
Applied OT Moment, Mot = (F1*H)
My biggest concern is from Case 2. Each method gives different answers and will provide a different factor of safety against overturning. This isn’t covered in any references I have for retaining walls since we don’t typically have uplift loads on them. For any of you who do PEMBs, what do you use?
I know some of you might comment that the load directions wouldn’t make sense for typical PEMB reactions. My question is more to do with calculating the overturning and resisting moments, so don’t get mixed up about load directions.
Enercalc, Case 1:
Resisting Moment, Mres = L/2*(F2+w1+w2)
Applied OT Moment, Mot = F1*H
Enercalc, Case 2:
Resisting Moment, Mres = L/2*(w1+w2)
Applied OT Moment, Mot = (F1*H)+(F2*L/2)
-------------------------------------------------------------
Text Ref., Case 1: (Same as Enercalc)
Resisting Moment, Mres = L/2*(F2+w1+w2)
Applied OT Moment, Mot = F1*H
Text Ref., Case 2:
Resisting Moment, Mres = L/2*(w1+w2-F2)
Applied OT Moment, Mot = (F1*H)
My biggest concern is from Case 2. Each method gives different answers and will provide a different factor of safety against overturning. This isn’t covered in any references I have for retaining walls since we don’t typically have uplift loads on them. For any of you who do PEMBs, what do you use?
I know some of you might comment that the load directions wouldn’t make sense for typical PEMB reactions. My question is more to do with calculating the overturning and resisting moments, so don’t get mixed up about load directions.