Structural
Jun 30, 2013
594
I have a steel joist with calcs (from manufacturer) showing Fy=50ksi for webs and chords.
Pls recommend steel spec should I use to get Fy=50 ksi for reinforcement pieces:
1. round rods
2. angles
3. 1/8" to 1" plates
 
Replies continue below

Recommended for you

If I was reinforcing the webs, I would most likely use 36 ksi angles. If I was reinforcing the chords, I most likely would use 50 ksi plates.
 