edison123
Electrical
- Oct 23, 2002
- 4,427
Hi prc
After a very long time, I am designing a one-off lighting transformer 3-ph, 20 KVA, 480 V Delta / 400 V star, 60 Hz air cooled, indoor application.
With 1.5 T and a stacking factor of 0.95 , I got the following voltage/turn for different core cross section (all square CS with square coils)
A. 150 x 150 mm - 8.541 V/turn
B. 125 x 125 mm - 5.932 V/turn
C. 100 x 100 mm - 3.796 V/turn
1. Are the above volts/turn correct?
2. Which core cross section would you recommend, A, B, C or something else?
3. Is 1.5 T for modern M36 CRGO steel too low? Should I increase it to 1.7 T?
Thanks in advance.
Muthu
After a very long time, I am designing a one-off lighting transformer 3-ph, 20 KVA, 480 V Delta / 400 V star, 60 Hz air cooled, indoor application.
With 1.5 T and a stacking factor of 0.95 , I got the following voltage/turn for different core cross section (all square CS with square coils)
A. 150 x 150 mm - 8.541 V/turn
B. 125 x 125 mm - 5.932 V/turn
C. 100 x 100 mm - 3.796 V/turn
1. Are the above volts/turn correct?
2. Which core cross section would you recommend, A, B, C or something else?
3. Is 1.5 T for modern M36 CRGO steel too low? Should I increase it to 1.7 T?
Thanks in advance.
Muthu