Buildtech2
Mechanical
- Mar 6, 2012
- 158
I am presently doing hydraulic calculations for painting workshop. As per NFPA 33, A.9.4, the spray applications should be located only in buildings that are completely protected by an approved system of automatic sprinklers.
[F] 415.4 Automatic sprinkler system. Group H occupies shall be equipped throughout with an automatic sprinkler system in accordance with Section 903.2.5.
As per NFPA-13, it can be classified as an extra hazard, group-1.
Now my question is as follows:
Painting and sand blasting workshop is a small two story workshop. On first floor, we have small office and paint storage room and on ground floor we have painting workshop, office of painting, office area sand blasting.
Based on 9.2 sq.m are sprinkler coverage area and maximum area operation as 232 sq.m as per Extra Hazard, Group-1,25 sprinkler should be considered in the calculations but I cannot accommodate more than 12 sprinklers in any space either on first floor and on ground floor. Do I have to add sprinklers from other spaces in order to reach at maximum area operation as 232 sq.m. Please advise.
[F] 415.4 Automatic sprinkler system. Group H occupies shall be equipped throughout with an automatic sprinkler system in accordance with Section 903.2.5.
As per NFPA-13, it can be classified as an extra hazard, group-1.
Now my question is as follows:
Painting and sand blasting workshop is a small two story workshop. On first floor, we have small office and paint storage room and on ground floor we have painting workshop, office of painting, office area sand blasting.
Based on 9.2 sq.m are sprinkler coverage area and maximum area operation as 232 sq.m as per Extra Hazard, Group-1,25 sprinkler should be considered in the calculations but I cannot accommodate more than 12 sprinklers in any space either on first floor and on ground floor. Do I have to add sprinklers from other spaces in order to reach at maximum area operation as 232 sq.m. Please advise.