JBD
Electrical
- Nov 30, 2001
- 56
I have a customer that is trying to install a "maintenance bypass" transformer in parallel with his existing backup generator and normal utility feed.
The new transformer is fed from the same utility connection point as his existing transformers. All of the transformers are cast coil construction connected Delta-Wye, with 480Y/277V secondaries. The output phase rotation of the new transformer has been verified as equal to the existing 480V grid.
The problem is that the output phase voltages of the new transformer are "not in phase" with any of the existing (there are four) transformers. For example the voltage from A(new) to A'(existing) is 275V, A to B' is 277V, and A to C' is 551V. Swapping primary H1, H2, and H3 connections does nothing except change the phase rotation
I have asked for wiring diagrams of the new and existing transformers to see if there is a problem with additive or subtractive winding connections or if the transformer is really built as a wye-wye.
Any other thoughts?
The new transformer is fed from the same utility connection point as his existing transformers. All of the transformers are cast coil construction connected Delta-Wye, with 480Y/277V secondaries. The output phase rotation of the new transformer has been verified as equal to the existing 480V grid.
The problem is that the output phase voltages of the new transformer are "not in phase" with any of the existing (there are four) transformers. For example the voltage from A(new) to A'(existing) is 275V, A to B' is 277V, and A to C' is 551V. Swapping primary H1, H2, and H3 connections does nothing except change the phase rotation
I have asked for wiring diagrams of the new and existing transformers to see if there is a problem with additive or subtractive winding connections or if the transformer is really built as a wye-wye.
Any other thoughts?