I am designing a custom filtration system that will operate at 1,500 cfm. Static pressure is approximately 6" w.g.. The customer wants me to supply 2 blowers that will operate in parallel. The blowers will be controlled by VFD's. During normal operation, each blower will operate at reduced rpms to provide a total flowrate of 1500 cfm. If one of the blowers fails, the other will speed up, allowing the overall system to maintain a flowrate of 1,500 cfm.
I have never installed parallel blowers. Under normal operation, each blower will be required to move 750 cfm. I've calculated the pressure drop through the system at 750 cfm to be approximately 3" w.g.. I'm assuming I need to select a blower capable of operating at 750 cfm at 3" static, with the capability to ramp up to 1500 cfm at 6" static. Does this make sense?
I have never installed parallel blowers. Under normal operation, each blower will be required to move 750 cfm. I've calculated the pressure drop through the system at 750 cfm to be approximately 3" w.g.. I'm assuming I need to select a blower capable of operating at 750 cfm at 3" static, with the capability to ramp up to 1500 cfm at 6" static. Does this make sense?