This is a question based on a parallel connection of two four winding transformers and how they can be modeled in any load flow & short circuit software.
Recently I have seen the following 4-winding power transformer connection with closed buses in a large industrial plant. May be they are operating when everything is fine. Please visualize a situation where,
Four winding transformer A :
50/30/30 MVA/ 132-11 kV, Yyyd, OLTC on 132 kV side with usual 16 steps of +/- 1.25%.
Secondary S1, Tertiary T1 with a separate DELTA stabilizing winding.
S1 is connected to 11 kV secondary Bus B1A
T1 is connected to 11 kV secondary Bus B2A
Four winding transformer B :
50/30/30 MVA/ 132-11 kV, Yyyd, OLTC on 132 kV side with usual 16 steps of +/- 1.25%.
Secondary S2, Tertiary T2 with a separate DELTA stabilizing winding.
S2 is connected to 11 kV secondary Bus B1B
T2 is connected to 11 kV secondary Bus B2B
Bus Section Details:
11 kV Bus sections B1A & B1B are normally CLOSED by a 11 kV TIE circuit breaker.
11 kV Bus sections B2A & B2B are normally CLOSED by a 11 kV TIE circuit breaker.
But 11 kV Buses B1A/ B1B and B2A/ B2B are physically separated apart by about 10 m in the same 11 kV substation.
My concerns are,
1)How does the voltage is regulated on each 11 kV bus at 11 kV nominal with this parallel 4-winding transformer connection?
2)Is it reasonable to model this configuration as it is, in a load flow/ short cct software program?
3)Is this a standard connection/configuration? Any advantages and disadvantages or any practical difficulties?
Comments are welcome!
Regards!
Kiribanda
This is a question based on a parallel connection of two four winding transformers and how they can be modeled in any load flow & short circuit software.
Recently I have seen the following 4-winding power transformer connection with closed buses in a large industrial plant. May be they are operating when everything is fine. Please visualize a situation where,
Four winding transformer A :
50/30/30 MVA/ 132-11 kV, Yyyd, OLTC on 132 kV side with usual 16 steps of +/- 1.25%.
Secondary S1, Tertiary T1 with a separate DELTA stabilizing winding.
S1 is connected to 11 kV secondary Bus B1A
T1 is connected to 11 kV secondary Bus B2A
Four winding transformer B :
50/30/30 MVA/ 132-11 kV, Yyyd, OLTC on 132 kV side with usual 16 steps of +/- 1.25%.
Secondary S2, Tertiary T2 with a separate DELTA stabilizing winding.
S2 is connected to 11 kV secondary Bus B1B
T2 is connected to 11 kV secondary Bus B2B
Bus Section Details:
11 kV Bus sections B1A & B1B are normally CLOSED by a 11 kV TIE circuit breaker.
11 kV Bus sections B2A & B2B are normally CLOSED by a 11 kV TIE circuit breaker.
But 11 kV Buses B1A/ B1B and B2A/ B2B are physically separated apart by about 10 m in the same 11 kV substation.
My concerns are,
1)How does the voltage is regulated on each 11 kV bus at 11 kV nominal with this parallel 4-winding transformer connection?
2)Is it reasonable to model this configuration as it is, in a load flow/ short cct software program?
3)Is this a standard connection/configuration? Any advantages and disadvantages or any practical difficulties?
Comments are welcome!