Here is the problem (NEC 2012):
Generator normally operates in parallel with the power grid. Grid is at 12.47 kV with a wye-wye transformer going down to 480V.
The customer owns the transformer.
The original design had the N & G bonded at the wye wye transformer, the 480V breaker, and at the 480V MCC. The high and low side neutrals of the wye-wye are also connected
I should note there is no Neutral load at the plant
**The problem is the high neutral current, which is about 7-800A** The attached sketch was how the unit was installed. Granted, the wye-wye xfmr may exasperate this problem, but I am thinking of the following:
Option 1
-> Disconnect all of the N-G Bonds except at the xfmr
Option 2
->Add in a low resistance ground at the generator
->Disconnect the neutral except at the transformer & generator...........removing it at the panel.
Any suggestions?
Generator normally operates in parallel with the power grid. Grid is at 12.47 kV with a wye-wye transformer going down to 480V.
The customer owns the transformer.
The original design had the N & G bonded at the wye wye transformer, the 480V breaker, and at the 480V MCC. The high and low side neutrals of the wye-wye are also connected
I should note there is no Neutral load at the plant
**The problem is the high neutral current, which is about 7-800A** The attached sketch was how the unit was installed. Granted, the wye-wye xfmr may exasperate this problem, but I am thinking of the following:
Option 1
-> Disconnect all of the N-G Bonds except at the xfmr
Option 2
->Add in a low resistance ground at the generator
->Disconnect the neutral except at the transformer & generator...........removing it at the panel.
Any suggestions?