PrebenJakobsen
Electrical
- Dec 1, 2008
- 27
Hi all,
I have an offshore installation with seven 50Hz generators (3 to 7MW) that can run in parallel on a 6kV distribution system. They are all grounded by NER. (8,2 to 17,3 ohm)
The original installed generators has a winding pitch that produces 3rd harmonic and the new installed generator produces almost none which results in a high 3rd harmonic current that heats it's NER. We have made some measurements that shows variation depending on numbers of generators in parallel, load power factor etc. and the heat is substantial.
We are now trying to find the best way to solve the problem, and i can see IEEE C.62.92 gives some guidance on the issue. Which one should i buy? Does anyone have better references?
Best Regards
Preben Jakobsen
I have an offshore installation with seven 50Hz generators (3 to 7MW) that can run in parallel on a 6kV distribution system. They are all grounded by NER. (8,2 to 17,3 ohm)
The original installed generators has a winding pitch that produces 3rd harmonic and the new installed generator produces almost none which results in a high 3rd harmonic current that heats it's NER. We have made some measurements that shows variation depending on numbers of generators in parallel, load power factor etc. and the heat is substantial.
We are now trying to find the best way to solve the problem, and i can see IEEE C.62.92 gives some guidance on the issue. Which one should i buy? Does anyone have better references?
Best Regards
Preben Jakobsen