Hi Gianno
what you intend is done all the time. If possible it is best to have both pumps with similar shutoff heads otherwise extra care needs to be taken to avoid having one pump deadheading (zero flow) the other.
To prepare the combined QH curve, I plot the QH curve of both pumps on the same graph. Then for each head point I add the flow from the first pump to that of the second. This gives a much flatter curve, sometimes with a hump at the start if the pump shutoff heads are not the same.
When this is done, I check the NSPH, efficiency/power and minimum and maximum flow limit for each pump to pick likely trouble points. Then I overlay the system resistance curve (or system curve envelope in variable demand/pressure scenarios) and make sure I am not close to any trouble points. In some cases it may be necessary to turn off one pump as part of the control strategy/system.
It is nice to have matched pumps in a system with a single system curve, but with multiple system curves and no VSDs somtimes different sized/speed pumps are better. The jockey pump is an extreme example. At other times it is simply necessary to use what is available,and this may result in using odd sized pumps.
Impeller trimming sometimes helps overcome a particular problem, as does a speed change by pulley or motor change.
Cheers
Steve McKenzie