Hi looking to tap down two identical 11kV/415V transformers these will be done isolated one at a time, however they will need to be momentarily parallelled while they are at different taps I know the risk of circulating currents and fault rating risk of parallel fed LV switchboards. How can I pre-determine what the circulating currents may be to prevent risk of trip?
Has anyone experience of doing this before?
 
Replies continue below

Recommended for you

You can model the transformers as parallel impedances, with a voltage source in one parallel path equal to the no-load voltage difference between the two unequal ratio transformers.
 