sturr
Structural
- Oct 5, 2005
- 27
I design light gage steel curtain wall stud framing. Recently I have had to apply the 2003 IBC wind design for the first time. I chose to use the ASCE 7-02 analytical procedure because the IBC simplified method did not specifically address parapets under components and cladding. The ASCE method generated very high parapet load of about twice the typical wall load (much, much high than the old UBC loads), and I have verified my numbers using a "Guide" published by ASCE. This particular job has 9 foot cantilevred parapets.
My problem is this: This job has a "base" stud design (size, gage, and spacing) provided in the contract documents. I have found the wall design to be inadequate with respect to the parapets. After reporting the issue I was informed the IBC simplified method had been used and approved by the building department.
I don't believe the IBC simplified method can be used to determine parapet loading because it uses "net" pressures combining internal and external pressures. I believe parapets should be subject to windward and leward pressures simultaneously. Which is also why I believe the simplified method does not address parapets.
Can anyone out there back me up on this or provide some insight into this topic? Before I cause a major change order, I want to make sure I'm not way off here.
THANK YOU!
My problem is this: This job has a "base" stud design (size, gage, and spacing) provided in the contract documents. I have found the wall design to be inadequate with respect to the parapets. After reporting the issue I was informed the IBC simplified method had been used and approved by the building department.
I don't believe the IBC simplified method can be used to determine parapet loading because it uses "net" pressures combining internal and external pressures. I believe parapets should be subject to windward and leward pressures simultaneously. Which is also why I believe the simplified method does not address parapets.
Can anyone out there back me up on this or provide some insight into this topic? Before I cause a major change order, I want to make sure I'm not way off here.
THANK YOU!