I am having a disagreement with another electician over the size of internal windings in a part winding start motor. He claims the start windings are wound with larger wire since they experience a higher current inrush. All my literature says the motor draws approximately 65% inrush at start up and cannot find any information on the windings. Can you help me settle this.
Thank you in advance,
viperone.
 
Replies continue below

Recommended for you

Hi.
Part start windings normally use the same size conductors, but only use a % of the winding on start up.....i.e. 60/40....using 60% of the windings for a softer, or lower current start up.
hope this is of some help
Jeff
 
“A standard Part-Winding-Start induction motor is arranged so that one-half of its primary winding can be energized initially and, subsequently, the remaining half can be energized, both halves then carrying equal current (NEC 430-3).”

In general part-winding-start motors have the standard type and the winding almost that of a standard dual voltage motor.

Special applications could have variations of this “50% standard array”. Motors with two poles could develop cusps in the speed-torque curve when part-winding started.
 
Inrush current is not the primary determining factor in deciding on conductor size for motor windings. Continuous current is more relevant, inrush is used in a "double check" of sorts once the continuous current requirements are satisfied. It is also incredibly impractical for a motor manufacturer to switch wire sizes when winding a stator so they will be the same size, selected based on the worst-case continuous current application.

Your buddy is wrong. He buys the next beer.

"Venditori de oleum-vipera non vigere excordis populi"


 
to viperone:

There is one case where the part winding start leads are larger. For 9-lead, delta connected, dual voltage, suitable for PWS on the low voltage, the 1-2-3 leads are normally larger than the remaining 6 leads. However this is for cost reasons rather than current sizing

Also some modern motors do not use true "part" windings anymore. They use a center tapped delta -- which uses the whole winding to start, but has the characteristics of a true "part" winding. This confuses some electricans who expect a split winding and find continuity on all leads.

to jrael:

There are some special application motors which must be sized for starting --- high inertia centrifuges comes to mind.

to aolalde:

There are other fractional part winding starts -- i.e. 2/3 part winding, where the current balance is unequal.

to motorsdirect:

I would be interested in seeing a 60/40 connection.


 