On with some maintenance on an 11kV board.
Knowns - we know the utility supply cable is in poor state but that's their cables.
our incoming switch is out of the board.
The bushings have been examined and are as new.
Connections at the back are shrouded but appear good and have not been touched.
The utility supply has been restored but our breaker is still out of the board.
A hissing noise can be heard in the panel
Using a TEV PD tester the dB reading is off scale on the yellow / L2.
We know the cable fault is on red L1.
We know there is a buried joint about 20m away.
The feeder cable is about 1700m long and is clearly jointed underground.
Question - If we had a fault on the cable about 20m from the board would that be picked up on L2 or because its hissing would that suggest its at the board.