ASCE 7-10 4.3.2 provisions for partitions
Exception: A partition live load is not required where the minimum specified live load exceeds 80psf.
For a second floor office if one were to use the office loading (50psf) the 15 psf load would need to be added. Where corridors are not defined and could possibly move, I tend to just use a blanket 80psf for the floor load. Technically 80 doesn't exceed 80 so does the partition live load of 15psf need to be added to this? Seems silly to bump it up to 95psf. To me if there is a corridor there isn't a possibility of a partition wall. The corridor walls would be the beginning of the "office space" so it would not be under the corridor load anymore. Thoughts?
Exception: A partition live load is not required where the minimum specified live load exceeds 80psf.
For a second floor office if one were to use the office loading (50psf) the 15 psf load would need to be added. Where corridors are not defined and could possibly move, I tend to just use a blanket 80psf for the floor load. Technically 80 doesn't exceed 80 so does the partition live load of 15psf need to be added to this? Seems silly to bump it up to 95psf. To me if there is a corridor there isn't a possibility of a partition wall. The corridor walls would be the beginning of the "office space" so it would not be under the corridor load anymore. Thoughts?