I'm wondering how you account for loading at tall, interior party walls for residential construction.
By Canadian code all party walls must be able to take 10psf without structural failure of the wall or any supporting members (ULS), this accounts for fire fighting equipment (ie. water) hitting the wall.
Now, do you consider deflection as a failure mode? I have been, but the more I think about this - the more I want to ignore deflection on these.
-If the wall works to support the roof without gypsum sheathing, and while it is deflected it has served the purpose(assuming once the wall deflects & water hits it the drywall is toast).
-As long as the wall deflects less than an inch it isn't going to hit the neighbouring wall, and if it does you get more rigidity.
The only arguments against this I can think of is after a fire they might have to rebuild the wall completely if the studs are damaged from excess defl'n, and of course saying code is code, and L/360 is your absolute under these conditions.
Thoughts?
edit: Common example of this would be a multi-family where a unit has a stairwell opening on an interior wall adjacent to another unit
I'm wondering how you account for loading at tall, interior party walls for residential construction.
By Canadian code all party walls must be able to take 10psf without structural failure of the wall or any supporting members (ULS), this accounts for fire fighting equipment (ie. water) hitting the wall.
Now, do you consider deflection as a failure mode? I have been, but the more I think about this - the more I want to ignore deflection on these.
-If the wall works to support the roof without gypsum sheathing, and while it is deflected it has served the purpose(assuming once the wall deflects & water hits it the drywall is toast).
-As long as the wall deflects less than an inch it isn't going to hit the neighbouring wall, and if it does you get more rigidity.
The only arguments against this I can think of is after a fire they might have to rebuild the wall completely if the studs are damaged from excess defl'n, and of course saying code is code, and L/360 is your absolute under these conditions.
Thoughts?
edit: Common example of this would be a multi-family where a unit has a stairwell opening on an interior wall adjacent to another unit