Does anyone have a link or source where one might view previous versions of the NEC? I used to keep many of these but they haven't survived my last few office moves. I am looking for the 1982 version of the NEC.
The reason is that we are doing a major overhaul of a major airport terminal built in 1983-84. The power distribution is set up so that feeders to panels from the main distribution panels are set up as risers. Power is fed at 480V/3ph/4w from a main substation to Distribution panels in electrical rooms where transformers 480-208y/120v/3ph/4w feed local branch circuit panels.
The problem we are having is that the initial feed say from a level 1 distribution board to a level 2 panel is with 4#350mcm, feeds a 225 Amp, 480y/277v/3ph/4w panel equipped with a side wiring gutter. There, a 4#4/0 feeder is tapped to it in the gutter and then proceeds to level 3, (around 65' in length), to feed another 225A branch panel without overcurrent protection. This violates the NEC tap rules in the current code, (NEC 240-21(b)). Although I do not know how the code read that was in effect back then, I don't think it was very much different than it is now.
Do one of you gents with better knowledge of past codes know of a provision that would allow this? This is in a major metropolitan area with notoriously stringent codes and AHJ inspectors,( whom of course have noticed this condition), and do not want to listen to our arguments that it has been this way, running fine for over 20 years and we are not budgeted to rebuild the entire 500,000 square foot terminal buildings' distribution systems.
So if you have a link to where I can find this old code, or if you've run into this type of installation, your assistance would be greatly appreciated. Sincere thanks in advance.
EEJaime
The reason is that we are doing a major overhaul of a major airport terminal built in 1983-84. The power distribution is set up so that feeders to panels from the main distribution panels are set up as risers. Power is fed at 480V/3ph/4w from a main substation to Distribution panels in electrical rooms where transformers 480-208y/120v/3ph/4w feed local branch circuit panels.
The problem we are having is that the initial feed say from a level 1 distribution board to a level 2 panel is with 4#350mcm, feeds a 225 Amp, 480y/277v/3ph/4w panel equipped with a side wiring gutter. There, a 4#4/0 feeder is tapped to it in the gutter and then proceeds to level 3, (around 65' in length), to feed another 225A branch panel without overcurrent protection. This violates the NEC tap rules in the current code, (NEC 240-21(b)). Although I do not know how the code read that was in effect back then, I don't think it was very much different than it is now.
Do one of you gents with better knowledge of past codes know of a provision that would allow this? This is in a major metropolitan area with notoriously stringent codes and AHJ inspectors,( whom of course have noticed this condition), and do not want to listen to our arguments that it has been this way, running fine for over 20 years and we are not budgeted to rebuild the entire 500,000 square foot terminal buildings' distribution systems.
So if you have a link to where I can find this old code, or if you've run into this type of installation, your assistance would be greatly appreciated. Sincere thanks in advance.
EEJaime