PCA Rentangular Tanks Design - Question about Example(SIMPLE)

Status
Not open for further replies.

KOJUNGMO

Civil/Environmental
Jul 6, 2014
17
I have a question about the PCA Rentangular Tank Example.

In the First Example

Design Information
Dimension : 30ft X 20ft X 10 ft
Wall thickness : 18 in.

There is Shear Strength (Vc)
Vc = 2 X [fc][/0.5] X b X d -> I belive that it has came from ACi 350-06 11.3.1.1
d = effective depth = thickness wall - cover - db/2 = 18 - 2 - 5/16 = 15.7 in.
Vc = 2 X [4000][/0.5] X 12 X 15.7

What I'd like to ask you is "12". Where does this value(12) come from???

Thank you for reading this.
 
Replies continue below

Recommended for you

CELinOttawa
Ah!!! Thanks! I'm not quite used to use US unit. So sorry for the silly question.
 
To paraphrase the wise: There are no silly questions, there are only unasked technical questions which then morph into legal ones...
 