Gauss2k
Electrical
- Feb 27, 2004
- 49
Hello everyone,
We just tested 2 PCB transformers: ratio, winding resistance, PCB dielectric breakdown and insulation test (megger @ 1kV).
All the tests gave good results on both transformers, but the insulation tests we're pretty low on -both- transformers primary side (about 8 to 9 MegOhm for a 25kV primary side).
The test instrument was working well because we tested surge arresters minutes later and they gave high results. The tests were indoor and the humidity level was not high.
Is there any special conditions or internal configuration in PCB transformers that could explain those results?
Thank you!
We just tested 2 PCB transformers: ratio, winding resistance, PCB dielectric breakdown and insulation test (megger @ 1kV).
All the tests gave good results on both transformers, but the insulation tests we're pretty low on -both- transformers primary side (about 8 to 9 MegOhm for a 25kV primary side).
The test instrument was working well because we tested surge arresters minutes later and they gave high results. The tests were indoor and the humidity level was not high.
Is there any special conditions or internal configuration in PCB transformers that could explain those results?
Thank you!