In a general manner, the power delivered by a hydraulic turbine is:
P = ?t * ?g * ?tr * 9,81 * Qd * Hn [kW]
Where: ?t = turbine efficiency.
?g = generator efficiency.
?tr = transformer efficiency.
Qd = design flow, [m³/s].
Hn = Net head, [m].
Where: Hn = H gross – ? hf
H gross = Gross head, [m].
hf = Head losses, [m].
Being for a Pelton turbine:
? hf = h friction losses + h minor losses + h manifold losses + h jets loss
I have designed a spreadsheet to calculate that power, taking into account all the variables indicated above.
I have tested the accuracy of my spreadsheet against the calculations achieved during the design of small hydro power plants that have been running since several years ago and, for my surprise, I have found that for the calculations of ? hf, they have NOT taken h jets loss, that is a loss of around 6% of the Gross Head.
My question is: why is it possible that for the power calculation, sometimes h jets loss is taken into consideration and, sometimes it is left aside?
For a particular calculation, P = 10000 kW without h jets loss, and P results to be 9328 kW if h jets loss is added to the equation.
I will appreciate very much your feedback on this matter. Thanks.
In a general manner, the power delivered by a hydraulic turbine is:
P = ?t * ?g * ?tr * 9,81 * Qd * Hn [kW]
Where: ?t = turbine efficiency.
?g = generator efficiency.
?tr = transformer efficiency.
Qd = design flow, [m³/s].
Hn = Net head, [m].
Where: Hn = H gross – ? hf
H gross = Gross head, [m].
hf = Head losses, [m].
Being for a Pelton turbine:
? hf = h friction losses + h minor losses + h manifold losses + h jets loss
I have designed a spreadsheet to calculate that power, taking into account all the variables indicated above.
I have tested the accuracy of my spreadsheet against the calculations achieved during the design of small hydro power plants that have been running since several years ago and, for my surprise, I have found that for the calculations of ? hf, they have NOT taken h jets loss, that is a loss of around 6% of the Gross Head.
My question is: why is it possible that for the power calculation, sometimes h jets loss is taken into consideration and, sometimes it is left aside?
For a particular calculation, P = 10000 kW without h jets loss, and P results to be 9328 kW if h jets loss is added to the equation.
I will appreciate very much your feedback on this matter. Thanks.